More VFD problems.
I appreciate the help and timely reply in another post earlier on about VFD's. I have wired up the VFD and attempted to start the Lathe motor. No start, no noise trying to start. All parameters correctly set, with the exception of "A"- output amps. The readout says 1.2 amps and We cannot seem to change it. I have the Hyanyang model for a 7.5 HP, single phase in 3 phase out. Motor is a 7.5 Hp, 220 3 phase, 23 amp, 1720 Rpm. At 1.2 amp output would the motor at least hum or slightly try to start?0527151448-00.jpg0527151448-00.jpg How do I proceed from here?
-
29th May 2015 01:44 AM # ADSGoogle Adsense Advertisement
- Join Date
- Always
- Location
- Advertising world
- Posts
- Many
-
29th May 2015, 02:06 AM #2GOLD MEMBER
- Join Date
- Jul 2010
- Location
- Melbourne
- Posts
- 7,775
Its late here.
I'm not sure what 340.3 means............its not HZ is it? You havent got base freq set at 400hz have you?
I think we'll need a list of your parameters to help.
What parameter is "A" you are talking about?
Good luck, cya in the morning lol
Stuart
-
29th May 2015, 06:29 AM #3Intermediate Member
- Join Date
- Dec 2011
- Location
- Lancaster, Ohio, USA
- Posts
- 36
Here are the parameters I have:
PD 001=0
pd 003=60
pd 004=60
pd 005=60
pd 008=220
pd 013=00
pd 014=3
pd 015=3
pd 023=0
pd 044=02
pd 045=03
pd 141=220
pd 142=23 (amps to motor)
pd 143=4
pd 144=1720
pd 151=0 (energy saver)
Hertz a=336
A Rott=12.
I have a Huanyang VFD, Model HYO5D523B. It is rated for a 7.5 HP motor, which is what the name plate says. 220 single phase imput, 220 3 phase output wanted. Motor plate says 23 amps. Vfd is 25 amps. The only problem I see is that DC output seems to be 377 volts, NO DC is wanted or needed. Ac amps output seems to be 1.2 amps as per the digital readout. We tried to change it without any success. The motor does not even try to start, no hum or anything else. There is a suds pump on the lathe rated at 1/2 HP, and it does not try to run either, I have not heard it run. The lathe was started and run for about 5 minutes when I bought it. Where to start troubleshooting?
-
29th May 2015, 09:34 AM #4.
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 27,798
First thing sI would do is reset everything on the VFD and try a smaller (~1HP) motor.
It absolutely has to have a DC V to generate the 3 phase. That is what a VFD does, it converts 1P AC to DC to 3P AC.
The "u" with the bar on top on the display is the DC voltage.
What is confusing to me is the u-bar should be accompanied by the "A" and "RPM" lights on
When the Hz and A lights are on this refers to how many hours the VFD has been on
Anyway try the reset and a small motor.
-
29th May 2015, 01:34 PM #5Intermediate Member
- Join Date
- Dec 2011
- Location
- Lancaster, Ohio, USA
- Posts
- 36
I have no other motor, smaller or otherwise. There is a 1/2 hp coolant motor that also refuses to start.
-
29th May 2015, 01:55 PM #6GOLD MEMBER
- Join Date
- Jul 2010
- Location
- Melbourne
- Posts
- 7,775
Can you explain what numbers you get on the display when you first turn the VSD(input) on and what is displayed when you press the run button.
I assume you aren't trying to use external switching?
I assume the motor it wired directly to the VSD?
Stuart
-
29th May 2015, 03:05 PM #7Intermediate Member
- Join Date
- Dec 2011
- Location
- Lancaster, Ohio, USA
- Posts
- 36
The motor is wired directly to the VFD. The numbers I get on start up are: Power light on, forward light blinks,display is A 000.0. "A" light is on.
Press run and I get A 000.8. Upon shutdown I get a display of E.L.U.N. then powers off.
-
29th May 2015, 07:24 PM #8.
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 27,798
Did you try the factory reset?
-
29th May 2015, 08:29 PM #9Cba
- Join Date
- Aug 2007
- Location
- Melbourne
- Age
- 68
- Posts
- 1,417
I see that you live in the US, where the 220V to your home are made by a center tapped transformer somewhere down the road of 2 times 110V which are out of phase by 180 degrees. In order to really get 220V to the VFD, it is necessary that the two wires going to the VFD are indeed 180 degree out of phase. If you wire them up to be in phase, you will not get 220V. I think that could be your problem, because your ELUN error is a DC bus undervoltage problem. Check the wiring in your fuse box, check the contactor that supplies your vfd power point.
We in Australia (and in Europe) do not use center tapped transformers of two times 110V and 180 degrees apart to provide a two phase 220 or (230 or 240) V to the home. We use another system where three phases are each 120 degrees apart and each have 230V to neutral and 400V between each other. That is why you are likely to get far better support from people in North America that are more familiar with your particular mains power distribution system and the contactors that go with it.
EDIT: the answer to your problem could be on page 2 of this thread: http://www.cnczone.com/forums/printt...9&pp=12&page=1
-
30th May 2015, 12:50 AM #10Intermediate Member
- Join Date
- Dec 2011
- Location
- Lancaster, Ohio, USA
- Posts
- 36
Interesting results, I took the receptacle out of its box to get a good connection and the results are as follows: wire # 1 to neutral =407, wire #2 to neutral= 433, wire #3 to neutral= 002. The numbers slowly change, never remaining still. from a high of 433 back down to 117. Does not sound right.
-
30th May 2015, 04:58 AM #11Intermediate Member
- Join Date
- Dec 2011
- Location
- Lancaster, Ohio, USA
- Posts
- 36
Checking as You asked: from power line to neutral is 117 for both wires, across both wires is 237. Sounds right.
-
30th May 2015, 11:24 AM #12
Can I ask where you bought this VFD or if you know of any major sellers that stock it?
I have been looking for one of these for a long time now and have not found any that are 220/240v in. I have a 5.0 Hp unit running my lathe which has a 7.5 Hp motor. I can only get about 80Hz (1600rpm) before the VFD shuts down. The lathe is designed to run at the equivalent of 100Hz (2000rpm). It has a 2 speed motor.
Dean
-
30th May 2015, 01:20 PM #13Intermediate Member
- Join Date
- Dec 2011
- Location
- Lancaster, Ohio, USA
- Posts
- 36
After spending most of the afternoon on the internet learning about VFD's, I called several companies and talked to tech support. Several people told Me that VFD's and rotary converters must be down sized when used with single phase imputs. Several people wanted to sell Me a 15hp rotary converter to run My 7.5hp lathe. One person said if I don't regularly bog the lathe down I could get by with a 10 hp rotary. Now the Asian Company responds that they will sell Me the next size larger VFD, which is 10 hp for $420, a rotary converter would be a sale price of $750, which includes shipping. The tech says the rotary is made from stock parts which means I can buy repair parts elsewhere. If I buy the rotary converter I feel I would be fortunate getting My money back for the VFD from the big auction site. Trying to decide what is more important, save money now with possible problems sooner or later, or spend the money, scream loud and long and hopefully no problems forever more.
-
30th May 2015, 03:20 PM #14Cba
- Join Date
- Aug 2007
- Location
- Melbourne
- Age
- 68
- Posts
- 1,417
HY05D523B means according to the user manual
HY trade mark
05D5 means the capacity, 5.5kW
23 means voltage rating, 1 or 3 ohase 220V
B is the software version
This inverter will only deliver 5.5kW if hooked up 3-phase 220V. It must be derated if hooked up dingle phase, because only one of its three input rectifiers must carry the whole current, and because the filter capacitors will be too small to cope with the 3 times lower ripple frequency. Without bothering you with the derating formula, in most cases the VFD will only be able to drive a motor of half the HP that it could drive if it was hooked up three phase.
-
30th May 2015, 03:42 PM #15Intermediate Member
- Join Date
- Dec 2011
- Location
- Lancaster, Ohio, USA
- Posts
- 36
I have had flurry of emails back and forth with the company I bought the VFD from. They have agreed to take the unit back as defective and issue a refund. A company in the next state makes rotary converters and I am thinking of getting one of them. My motor is 7.5hp. I will probably buy a 10hp converter, another web site claims a 7.5 hp rotary converter only puts out 6.7 hp. The tech says a lathe with a clutch is a much easier start than one with out. I don't see using 1/2 the hp on a regular basis. I will appreciate further advice or comments and will post the outcome when it arrives. Thanks all for the help, Mark.
Similar Threads
-
USB problems
By Harry72 in forum COMPUTERSReplies: 15Last Post: 14th October 2011, 05:38 PM -
OLD AGE Problems
By gawdelpus in forum WOODIES JOKESReplies: 2Last Post: 16th February 2011, 01:07 PM -
IE Problems
By chrisb691 in forum COMPUTERSReplies: 10Last Post: 12th August 2007, 10:35 PM -
Various problems...
By CameronPotter in forum WOODTURNING - PEN TURNINGReplies: 6Last Post: 21st February 2006, 01:49 PM -
So you think you have problems.....?
By Breslauer in forum WOODIES JOKESReplies: 4Last Post: 16th September 2005, 08:36 PM