    Quote Originally Posted by Stustoys View Post
    Just so I've got it clear. If you start at say 100Hz then speed up to 200Hz with the pot, you cant go back down to 100Hz?

    Stuart

    Stuart G'day

    You are correct ..

    cant go back down using pot or if the pot is switched off with the down arrow..

    I just can't work out which pd function affects this...

    Which as you might imagine is totally annoying..

    Regards,

    Steve

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #17
    Join Date
    Jun 2008
    Location
    Victoria, Australia
    Age
    74
    Posts
    6,132

    Default

    Ok, this is getting strange, what are the decelleration times set to, PD15, PD17, PD19, PD21

    Ray

  4. #18
    Join Date
    Sep 2013
    Location
    melb
    Posts
    35

    Default

    Quote Originally Posted by RayG View Post
    Ok, this is getting strange, what are the decelleration times set to, PD15, PD17, PD19, PD21

    Ray
    Hey Ray G'day,

    Thank you for your post,

    Strange indeed...

    Ok

    PD15, PD17, PD19, PD21 are at default no value
    PD14, PD16, PD18, PD20 are at default also no value 0


    Cheers and ty,

    Steve

  5. #19
    Join Date
    Jul 2010
    Location
    Melbourne
    Posts
    7,775

    Default

    Thats strange. Min setting on mine is 0.1.

    Try setting them all to 5.

    Stuart

  6. #20
    Join Date
    Sep 2013
    Location
    melb
    Posts
    35

    Default

    Stuart G'day,

    Ok set all to 5, same difference.. going up good comming down not so good..

    Steve

  7. #21
    Join Date
    Jul 2010
    Location
    Melbourne
    Posts
    7,775

    Default

    I'm starting to wonder if your VSD is fried.
    If you'd like to make a list of all your PD settings I can compare them to the settings on mine, but I doubt we are going to find a magic number. I've been wrong before though.

    Stuart

  8. #22
    Join Date
    Sep 2013
    Location
    melb
    Posts
    35

    Default

    Quote Originally Posted by Stustoys View Post
    I'm starting to wonder if your VSD is fried.
    If you'd like to make a list of all your PD settings I can compare them to the settings on mine, but I doubt we are going to find a magic number. I've been wrong before though.

    Stuart
    Stuart G'day,

    Ok sounds like a plan, I'll do that first thing in the morning.. almost midnight..

    VSD fried who knows, but you made me go and smell it and it doesn't smell like its blown a gasket.

    I'm sure it has to be something so dam simple..

    Greatly appreciate your assist.

    Cheers.

    Steve

  9. #23
    Join Date
    Sep 2013
    Location
    melb
    Posts
    35

    Default

    Stuart G'day,

    As promised my settings.. I used a spreadsheet that I downloaded from this forum I believe and just filled out my numbers... cheers and again thank you for going to the trouble.

    Steve


    Code Function Set Range & Function Explanation Factory Setting
    PD000 Parameter Lock 0:Invalid 1:Valid 0
    PD001 Source of Run Commands 0:Operator 1:External terminal 0
    2:Communication port
    PD002 Source of Operating Frequency 0:Operator 1:External terminal 0
    2:Communication port
    PD003 Main Frequency 0.00~400.00 Hz 400
    PD004 Base Frequency 0.01~400.00 Hz 400
    PD005 Max Operating Frequency 50.00~400.00 Hz 400
    PD006 Intermediate Frequency 0.01~400.00 Hz 2.5
    PD007 Min. Frequency 0.01~20.00 Hz 0.2
    PD008 Max. Voltage 0.1V—* 220
    PD009 Intermediate Voltage 0.1V—* 15
    PD010 Min. Voltage 0.1~50.0V 8
    PD011 Frequency Lower Limit 0.00~400.00 Hz 120
    PD012 Reserved null
    PD013 Parameter Reset 00~10 08:Restore the factory setting. No other function. 0
    PD014 Accel. Time 1 0.1~6500.0S 10
    PD015 Decel. Time 1 0.1~6500.0S 10
    PD016 Accel. Time 2 0.1~6500.0S 20
    PD017 Decel. Time 2 0.1~6500.0S 20
    PD018 Accel. Time 3 0.1~6500.0S 40
    PD019 Decel. Time 3 0.1~6500.0S 40
    PD020 Accel. Time 4 0.1~6500.0S 80
    PD021 Decel. Time 4 0.1~6500.0S 80
    PD022 Reserved 0
    PD023 Rev. Rotation Select 0: Rev Run forbidden; 1:Rev Run Enable 0
    PD024 STOP key select 0:STOP Invalid 1:STOP Valid 1
    PD025 Starting Mode 0:Start from Starting Frequency 0
    1:Frequency track start
    PD026 Stopping Mode 0:Decelerating stop 1
    1:Coasting stop
    PD027 Starting Frequency 0.1~10.0 Hz 0.5
    PD028 Stopping Frequency 0.1~10.0 Hz 0.5
    PD031 DC Braking level 0.0~20.0% 2
    PD029 DC Braking time at start 0.0~25.0S 0
    PD030 DC Braking time at stop 0.0~25.0S 0
    PD032 Frequency track time 0.0~20.0S 5
    PD033 Current level for frequency track 0~200% 150
    PD034 Voltage rise time during frequency track 0.5
    PD035-PD040 Reserved null
    PD041 Carrier frequency 0~15 8
    PD042 Jogging Frequency 0.00~400.00 Hz 5
    PD043 S-Curve Time 0~6500S 0
    *PD044 Multi-input 1(FOR) 0: Invalid; 1:Run; 2: For rotation; 3: Rev rotation; 4: Stop; 5: FOR/REV.; 6: Jog; 7: Jog For rotation; 8: Jog Rev Rotation; 9: Emergent stop; 10: Reset; 11:Reserved; 12: Overheat of heat sink or motor; 17: High speed; Middle speed; 19: Low speed; 20: Multi-speed 1; 21: Multi-speed 2; 22: Multi-speed 3; 23: Ramp select 1; 24: Ramp select 2; 25: UP function; 26: DOWN function; 27: Counter 28: Counter reset; 29: Drawing; 32: PID Start 2
    *PD045 Multi-input 2(REV) 3
    *PD046 Multi-input 3(RST) 4
    *PD047 Multi-input 4(SPH) 7
    *PD048 Multi-input 5(SPM) 19
    *PD049 Multi-input 6(SPL) 20
    *PD050 Multi-output 1(DRV) 0: Invalid; 1: Run; 2: Fault indication; 3: Zero Speed; 4: Braking indication; 5: Set Frequency reach; 6: Arbitrary Frequency 1 reach; 1
    *PD051 Multi-output 2(UPF) 3
    *PD052 Multi-output 3(Terminals of FA,FB,FC) 1
    *PD053 Multi-output 4(Terminals of KA,KB) 7: Arbitrary Frequency 2 reach; 8: In Accel.; 9: In Decel.; 10: Inverter Overload alarm; 11: Motor Overload alarm; 12: Over-torque alarm; 13: Low voltage alarm; 14: Single stage end indication; 15: Process end indication; 16: Counter reach; 27: Drawing reach; 28:PID lower limit alarm; 29: PID upper limit alarm; 30: Fan act; 31: Reserved; 32: Braking resistor act 3
    PD054 Multi-output 5(AM) Output of digital frequency signals 0
    PD055 AM Analog output Gain 0.0~100.0% 100
    PD056 Skip Frequency 1 0.00~400.00 Hz 0
    PD057 Skip Frequency 2 0.00~400.00 Hz 0
    PD058 Skip Frequency 3 0.00~400.00 Hz 0
    PD059 Skip Frequency Range 0.00~2.00 Hz 0.5
    PD060 Uniform Frequency 1 0.00~400.00 Hz 0
    PD061 Uniform Frequency 2 0.00~400.00 Hz 0
    PD062 Uniform Frequency Range 0.10~10.00 Hz 0.5
    PD063 Timer 1 time 0~10.0 0.1
    PD064 Timer 2 time 0~100 0.01
    PD065 Counting value set 00~65500 0
    PD066 Intermediate Counter 0~65500 0
    PD067-PD069 Reserved
    PD070 Analog Input 0~10 0
    PD071 Analog Filtering Constant 0~50 20
    PD072 50
    PD073 Bias Direction at Higher Frequency 0.00~400.00 Hz 0
    PD074 0
    PD075 0:Positive direction 1:Negative direction 0
    PD076 Analog Negative Bias Reverse 0:Not allowable. 1:Allowable. 0
    PD077 Up/Down Function 0:Not memorized 1:Memorized 0
    PD078 Up/Down Speed 0:0.01HZ 1:0.1HZ 0
    PD079 Reserved 0.01
    PD080 PLC Operation 0:Normal run; 1: External control 4 -speed; 2:External control multi-speed; 3: Disturbance; 4: Internal control multi-speed; 5: Drawing 0
    PD081 AutoPLC 0:Stop after running for one cycle; 1:Cycling run; 2:Auto stop after running for one cycle (STOP for intervention); 3: Auto Run and Cycling (STOP for intervention) 0
    PD082 PLC rotation Direction 0~255 (0:For 1:Rev) 0
    PD083 0~255 (0:For 1:Rev)
    PD084 PLC Ramp Time 0~65535 0
    PD085 0~65535
    PD086 Frequency 2 0.00-400.00 Hz 15
    PD087 Frequency 3 0.00-400.00 Hz 20
    PD088 Frequency 4 0.00-400.00 Hz 25
    PD089 Frequency 5 0.00-400.00 Hz 30
    PD090 Frequency 6 0.00-400.00 Hz 35
    PD091 Frequency 7 0.00-400.00 Hz 40
    PD092 Frequency 8 0.00-400.00 Hz 0.5
    PD093 Frequency 9 0.00-400.00 Hz 10
    PD094 Frequency 10 0.00-400.00 Hz 15
    PD095 Frequency 11 0.00-400.00 Hz 20
    PD096 Frequency 12 0.00-400.00 Hz 25
    PD097 Frequency 13 0.00-400.00 Hz 30
    PD098 Frequency 14 0.00-400.00 Hz 35
    PD099 Frequency 15 0.00-400.00 Hz 40
    PD100 Frequency 16 0.00-400.00 Hz 45
    PD101 Timer 1 0.0-6500.0S 10
    PD102 Timer 2 0.0-6500.0S 10
    PD103 Timer 3 0.0-6500.0S 0
    PD104 Timer 4 0.0-6500.0S 0
    PD105 Timer 5 0.0-6500.0S 0
    PD106 Timer 6 0.0-6500.0S 0
    PD107 Timer 7 0.0-6500.0S 0
    PD108 Timer 8 0.0-6500.0S 0
    PD109 Timer 9* 0.0-6500.0S 0
    PD110 Timer 10 0.0-6500.0S 0
    PD111 Timer 11 0.0-6500.0S 0
    PD112 Timer 12 0.0-6500.0S 0
    PD113 Timer 13 0.0-6500.0S 0
    PD114 Timer 14 0.0-6500.0S 0
    PD115 Timer 15 0.0-6500.0S 0
    PD116 Timer 16 0.0-6500.0S 0
    Code Functions Set Range & Function Explanation Factory Setting
    PD117 AutoPLC Memory 0~1 0
    PD118 Over-voltage Stall Prevention 0:Invalid 1:Valid 1
    PD119 Stall Prevention Level at Accel. 150
    PD120 Stall Prevention Level at Constant Speed 0~200% 0
    PD121 Stall Prevention Level at Decel. 0~200% 5
    PD122 0~200% NULL
    PD123 Over-torque Detect Mode 0~3 0
    PD124 Over-torque Detect Level 0~200% 0
    PD125 Over-torque Detect Time 0.1~20.0S 1
    PD126 0
    PD127-PD129 Reserved NULL
    PD130 Number of Auxiliary Pump 0~2 0
    PD131 Continuous Operating Time of Aux. Pumps 1~9000mim 60
    PD132 Interlocking Time of Aux. Pumps 1~250s 5s
    PD133 High Speed Running Time 1~250s 60s
    PD134 Low Speed Running Time 1~250s 60s
    PD135 Stopping Voltage Level 1~150% 95%
    PD136 Lasting Time of Stopping Voltage Level 1~250s 30s
    PD137 Wakeup Level 1~150% 80%
    PD138 Sleep Frequency 0.00~400.0 0
    PD139 Lasting Time of Sleep Frequency 1~250s 20s
    PD140 Reserved NULL
    PD141 Rated Motor Voltage Set according to Motor nameplate 220
    Set according to Motor nameplate
    PD142 Rated Motor Current 02—10 5
    00—9999
    PD143 Motor pole number. 2
    PD144 Rated Motor Revolution 3000
    PD145 Auto Torque Compensation 0.1—10.0 % 2.00%
    PD146 Motor no-load current 0—99 40
    PD147 Motor slip compensation 0.0—10.0 20
    PD148-PD149 Reserved
    PD153 Restart after Instantaneous Stop 0:Invalid 1:Frequency track 0
    PD152 1
    PD154 Allowable Power-Breakdown Time 0—10 0.5
    PD155 Number of Abnormal Restart 0:Invalid 1:Valid 0
    PD150 Auto Voltage Regulation 0~10% 1
    PD151 Auto Energy Saving 0
    PD156 Proportional Constant (P) 0.0~1000.00% 100%
    PD157 Integral Time (I) 0.1~3600.00S 5
    PD158 Differential Time (D) 0.01~10.00S 0
    PD159 Target value 0.0~100.0% 0
    PD160 Target value select 0: set by the operator 1:set by external terminals(0-10V) 0
    PD161 PID upper limit 0~100% 100%
    PD162 PID lower limit 0%
    PD163 Communication Addresses 0-250 0
    PD164 Communication Data Method 0-3 0
    PD165 0-5 0
    PD166 Voltage Rating of Inverter Set according to the model 0
    PD167 0
    PD168 0
    PD169 NULL
    PD170 Display Items 0-5 7
    PD171 Display Items Open 0-7 7
    PD172 0
    PD173 Rated Current of Inverter 255
    PD174 Set according to the model 7
    PD175 Inverter Model 0
    PD176 Inverter Frequency Standard 0:50Hz 1:60Hz 0
    PD177 Fault Record 1 LU
    PD178 Fault Record 2 Note: —— means no fault record. OL - 1
    PD179 Fault Record 3 LU
    PD180 Fault Record 4 DL
    PD181 Software Version U - 1.00
    PD182 Manufacture Date Year:Month:Week 30627
    PD183 Serial No. 65535
    PD184 20
    PD185 0
    PD186 0
    PD187 NULL
    NULL
    NULL

  10. #24
    Ueee's Avatar
    Ueee is offline Blacksmith, Cabinetmaker, Machinist, Messmaker
    Join Date
    Dec 2011
    Location
    Canberra
    Age
    40
    Posts
    4,467

    Default

    Hi,
    What sort of motor is it?
    Looks like you need to change your main and base frequencies 003 and 004. Also try changing 026 to 0, that way you will get deceleration when changing speeds down so you should really notice if it is working.

    Ew
    1915 17"x50" LeBlond heavy duty Lathe, 24" Queen city shaper, 1970's G Vernier FV.3.TO Universal Mill, 1958 Blohm HFS 6 surface grinder, 1942 Rivett 715 Lathe, 14"x40" Antrac Lathe, Startrite H225 Bandsaw, 1949 Hercus Camelback Drill press, 1947 Holbrook C10 Lathe.

  11. #25
    Join Date
    Sep 2013
    Location
    melb
    Posts
    35

    Default

    Quote Originally Posted by Ueee View Post
    Hi,
    What sort of motor is it?
    Looks like you need to change your main and base frequencies 003 and 004. Also try changing 026 to 0, that way you will get deceleration when changing speeds down so you should really notice if it is working.

    Ew

    Hey Uee G'day,

    Thank you for your post,

    Ok motor is a water cooled spindle, 1.5kw 400mh - 5amp 24000 rpm its a GZD-80

    if I change 026 to 0 then the stop button on the panel doesnt work... the spindle wont power down just keeps spinning 026 to 1 panel stop works as intended.

    when you say change main and base frequencies 003/004 as I understand it 003 is for frequency you want the spindle to start up at 100/200/300 (whatever number) and 003 is what you are in actually fact adjust when using the up and down arrow keys on the panel - when I use the panel using the up arrow key increasing the numbers the spindle responds and speeds up - using the down arrow key only the numbers change but spindle speed doesnt..

    004 should then be set at ???? 005 i would be right at assuming is the rated mh of the spindle which in my case is 400

    Thank you for your input.

    Steve

  12. #26
    Join Date
    Jul 2010
    Location
    Melbourne
    Posts
    7,775

    Default

    I dont think changing base freq is a good idea.

    of to the shed back soon

  13. #27
    Ueee's Avatar
    Ueee is offline Blacksmith, Cabinetmaker, Machinist, Messmaker
    Join Date
    Dec 2011
    Location
    Canberra
    Age
    40
    Posts
    4,467

    Default

    Well i've lost my book so i'm next to useless....

    026 should not change how the stop button works, just how the motor slows down.

    Ew
    1915 17"x50" LeBlond heavy duty Lathe, 24" Queen city shaper, 1970's G Vernier FV.3.TO Universal Mill, 1958 Blohm HFS 6 surface grinder, 1942 Rivett 715 Lathe, 14"x40" Antrac Lathe, Startrite H225 Bandsaw, 1949 Hercus Camelback Drill press, 1947 Holbrook C10 Lathe.

  14. #28
    Join Date
    Jul 2010
    Location
    Melbourne
    Posts
    7,775

    Default

    Well I cant see anything wrong.

    There are some numbers that are different of course. Long shot PD138 you have as 0, my VSD and manual say 20..........I'm not even sure what it does.

    I'll type up the rest after breakfast lol

    Stuart

  15. #29
    Join Date
    Jun 2008
    Location
    Victoria, Australia
    Age
    74
    Posts
    6,132

    Default

    Hi Stuart, I set the sleep frequency to Daily...

    AFAIK It's used when you have multiple pump systems.

    Not seeing anything obvious in that parameter list.

    Ray

  16. #30
    Ueee's Avatar
    Ueee is offline Blacksmith, Cabinetmaker, Machinist, Messmaker
    Join Date
    Dec 2011
    Location
    Canberra
    Age
    40
    Posts
    4,467

    Default

    Hi Steve,
    Is the motor base frequency 400Hz?

    I would try setting 003 to a lower setting and try it. maybe 300.

    Ew
    1915 17"x50" LeBlond heavy duty Lathe, 24" Queen city shaper, 1970's G Vernier FV.3.TO Universal Mill, 1958 Blohm HFS 6 surface grinder, 1942 Rivett 715 Lathe, 14"x40" Antrac Lathe, Startrite H225 Bandsaw, 1949 Hercus Camelback Drill press, 1947 Holbrook C10 Lathe.

Page 2 of 3 FirstFirst 123 LastLast

Similar Threads

  1. VFD settings HUANYANG
    By morrisman in forum METALWORK FORUM
    Replies: 25
    Last Post: 12th April 2012, 11:41 PM
  2. Settings
    By ahmmha in forum WELDING
    Replies: 0
    Last Post: 11th June 2011, 11:58 AM
  3. Mig settings for 6mm steel?
    By montiee in forum WELDING
    Replies: 6
    Last Post: 22nd September 2009, 08:47 PM
  4. Amp settings
    By Unit_01 in forum METALWORK FORUM
    Replies: 21
    Last Post: 22nd October 2007, 05:06 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •