    Quote Originally Posted by jack620 View Post
    Chris,
    Thanks for the explanation. To clarify- does the four-wire method use three logic inputs on my VFD, with the fourth wire being +24VDC?
    Yes, three inputs. The fourth wire is 24V.

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Age
    2010
    Posts
    Many





     
  3. #92
    Join Date
    Oct 2012
    Location
    Australia
    Posts
    765

    Default

    Quote Originally Posted by cba_melbourne View Post
    >...........I need to get my head around this 2-wire vs 3-wire control issue...........


    It is actually 3 or 4 wires (not 2 or 3 wires as I mentioned). But let me explain what I mean:

    3-wire start-stop control

    Imagine a VFD that is programmed to run forward, if you apply 24V to input 1. And it runs in reverse if you apply 24V to input 2. And it stops, if both inputs 1 and 2 are open. That is a total of 3 wires (+24V, run FWD, and run REV). If this control cable suffers a short circuit between +24 and any of the other two wires, the motor starts on its own with potentially dire consequences. If say the FWD wire breaks, you may have the operator leaving the main switch in FWD position and walk away, and when someone moves the broken wire it may make contact and the motor starts unexpectedly, with potentially bad consequences.


    4-wire start-stop control

    Imagine a VFD that is programmed to run only forward, if 24V is applied to BOTH input 1 (run FWD) AND input 3 (enable VFD). And it only runs backwards, if 24V is applied to BOTH input 2 (run REV) AND input 3 (enable VFD). Now a simple short between any two wires is not going to start the motor. And a broken fwd, rev or enable wire is going to cause the VFD to trip, so you need to turn it off and on again to restart (the software for 4-wire control regards any fwd or rev signal without enable signal as a potentially broken cable and locks the VFD. It also regards any FWD or REV signal with enable signal both active during power-on of the VFD as a broken wire and locks the VFD).

    Wire shorts usually happen when the control cable gets squashed. Wire breakage happens where control cables are continuously bent, or where cables are not properly finished/protected at the connector ends. Both problems are initially often only intermittant. The 4 wire method uses one extra input, it is still not 100% foolproof, but definitely safer than the 3 wire method. Me personally, I find this reason enough - but I concede that many low cost VFD have limited input lines, and the 4 wire method may mean to sacrifice another feature....

    Chris

    PS: I would personally not recommend to connect the chuck hood to an E-Stop, IF you are the sole user of this lathe. If other people use it too, then yes.

    Stop in 3 wire is "should be" normally closed, so that an open circuit should stop the motor, and start FWD/START REV are normally open, with starts interlocked with stop.

  4. #93
    Ueee's Avatar
    Ueee is offline Blacksmith, Cabinetmaker, Machinist, Messmaker
    Join Date
    Dec 2011
    Location
    Canberra
    Age
    40
    Posts
    4,467

    Default

    Ok....not sure what that was all about....

    This discussion has bought up some flaws in my system. I use a double pole double throw rotary switch. Rotate one way for forwards, other for reverse. The first pole signals the FWD and REV logic, the second pole signals the ON logic. If-the FWD wire was to break, i would have no forwards but still reverse. If the ON wire was to break i'd get nothing. But if the REV wire was to break i would get FWD with the switch in either position. This is because with no FWD or REV signal the huanyangs will run FWD with just the ON signal.

    As to the whole chuck coming off thing, my point is not to just set the VFD to 2 sec ramp down and try it. Start with a high number and work your way down. Same if you wish to use DC braking, start with the lowest voltage possible and go from there. With luck the worst you will do is overload the VFD, but if you are unlucky you may be playing a very scary round of classic catches.

    Cheers,
    Ew
    1915 17"x50" LeBlond heavy duty Lathe, 24" Queen city shaper, 1970's G Vernier FV.3.TO Universal Mill, 1958 Blohm HFS 6 surface grinder, 1942 Rivett 715 Lathe, 14"x40" Antrac Lathe, Startrite H225 Bandsaw, 1949 Hercus Camelback Drill press, 1947 Holbrook C10 Lathe.

  5. #94
    Join Date
    Nov 2007
    Location
    melbourne australia
    Posts
    2,643

    Default VFD switching on a Hercus 260

    Quote Originally Posted by Pete F View Post
    The first VFD I fitted I used CAT5 data cable in fact.
    My installation manual calls for thin gauge twisted pairs for control wiring, so I am planning to use Cat5 too.

    Chris,
    Thanks, that leaves me one logic input spare for e-stop.

  6. #95
    Join Date
    Aug 2008
    Location
    Oatley NSW
    Age
    69
    Posts
    244

    Default

    Hi jack620,
    I attach a quick diagram of what other members have beensaying to give you an idea of the control circuit that is being discussed. Ihave put the Emergency Stops into the VSD at Input 3 and in the program youwould need to make it an overriding command on Input 1 & 2 which are theForward & Reverse commands. This way you can set the amount of ramp up& down times for the three inputs and is in keeping with what other membersare saying about bringing the Lathe to a controlled stop in the threesituations.
    I would like to add that I would not wire the control this wayas I would use other methods to perform the Emergency Stop.
    You need to read the Altavar’s Manual closely as the Inputs1 to 4 are programmable and you need to set what type of Reset you want.
    The diagram is just simplistic and does not take intoaccount if you have other controls e.g. Light, Water etc.
    If you are not good at control circuits, sizing the CircuitBreaker etc I suggest you get an Industrial Electrician and you may need tospeak to a Schneider Drives Technical person about the program parameters ifyou are unsure, they are usually helpful on the phone.

    Regards,
    Keith_W.
    Attached Files Attached Files

  7. #96
    Join Date
    Nov 2007
    Location
    melbourne australia
    Posts
    2,643

    Default

    Hi Keith,
    thanks for going to the trouble. I started on the wiring this morning and I am doing exactly as you suggest with the addition of the original Hercus start button being connected to LI4. I will also include the original stop button in the series loop with the foot and headstock cover switches.

    That way the original controls function exactly as they always did. I just need to check out how to program the inputs to make this work. LI4 will need to be able to accept a momentary input.

    Chris

  8. #97
    Join Date
    Jun 2011
    Location
    Australia east coast
    Age
    71
    Posts
    1,469

    Default

    Quote Originally Posted by Ueee View Post
    Now why didn't I thinknk of that.........

    You clearly stated earlier in the thread that having a chuck come loose would not be a problem.
    No. He said that it had not been a problem ON HIS LATHE.

    Said lathe having same spindle nose etc as the one under discussion and fitted with working VFD.

    I have nothing to add as my lathes have either DIN or camlock spindle noses. Well, except for the Smith-Drum but adding a VFD to that one would be akin to applying lipstick to a pig.

    PDW

  9. #98
    Ueee's Avatar
    Ueee is offline Blacksmith, Cabinetmaker, Machinist, Messmaker
    Join Date
    Dec 2011
    Location
    Canberra
    Age
    40
    Posts
    4,467

    Default

    Quote Originally Posted by Pete F View Post
    You get what you pay for.

    Like Stuart, my e-stop and regular stop are the same. On the 260 it's a 2 second stop cycle, I can't recall what the other lathe is, I probably would have made them the same. I can't imagine a VFD being able to stop a lathe so suddenly it would unscrew a chuck, especially not without some pretty serious braking resistors. That energy needs to go somewhere.
    No mention of Pete's lathe only.

    This is now just a pointless waste of space on Chris's thread. Clearly the chuck will never unscrew from a hercus under vfd ramp down and braking. Since I don't own a hercus clearly I have no idea what I am talking about.
    1915 17"x50" LeBlond heavy duty Lathe, 24" Queen city shaper, 1970's G Vernier FV.3.TO Universal Mill, 1958 Blohm HFS 6 surface grinder, 1942 Rivett 715 Lathe, 14"x40" Antrac Lathe, Startrite H225 Bandsaw, 1949 Hercus Camelback Drill press, 1947 Holbrook C10 Lathe.

  10. #99
    Join Date
    Oct 2012
    Location
    Australia
    Posts
    765

    Default

    Here is a basic drawing for a 3 wire control. I'm not sure if it is totally applicable to the VFD and the existing controls.
    I could not see a circuit of the existing controls in the posts, did I miss it?

    -Josh
    Attached Files Attached Files

  11. #100
    Join Date
    Aug 2007
    Location
    Melbourne
    Age
    68
    Posts
    1,417

    Default

    The Altivar 12 has a nice extra feature called "decelleration ramp adaptation".
    In addition to normal time based ramp as fond on just any basic VFD, it has two more options that may be selcted instead:

    - It can automatically increase decelleration time when stopping high inertia load, to prevent DC bus overload. This means you always have the shortest possible stopping time, even when changing workpiece weight, without need to set manually a longer ramp time. This function is only available without an external brake resistor module.

    - Motor braking without the use of an external brake resistor. It makes use of motor losses to dissipate some of the regeneration energy.

    Both functions are new to me (my VFD's are all older models). Once you got it all setup and you had time to play around a bit, I would like to hear what you think about these two modes. Chris

  12. #101
    Join Date
    Nov 2007
    Location
    melbourne australia
    Posts
    2,643

    Default

    Thanks gents. The VFD is installed and "working". I have initially just configured it for 2-wire control via the rotary selector. It works in FWD, but not REV. I have checked and there is 24V on the logic input 2 when I select REV. I need to look at the settings for input 2.

    I have set max freq to 75Hz. That seems fast enough to me.

    Accel and decel are set to 2 seconds for now.

    Chris

  13. #102
    Join Date
    Jul 2010
    Location
    Melbourne
    Posts
    7,775

    Default

    Hi Chris,

    Do you have an parameter like "reverse rotation select"?

    Hard to help without the manual.

    Stuart

  14. #103
    Join Date
    Jul 2010
    Location
    Melbourne
    Posts
    7,775

    Default

    Found a manual. Assuming its the right one. You do have reverse inhibition but the default is no. Page 60 if I have the right manual.

    So no help there

    Stuart

  15. #104
    Join Date
    Nov 2007
    Location
    melbourne australia
    Posts
    2,643

    Default Success!

    Stuart,
    thanks for looking into it for me. There is a parameter called Reverse Direction (rrS) which selects the logic input assigned to the reverse command (page 66). Default is Inactive. It wasn't easy to find, nor is it intuitively named.

    The VFD is now fully functional. All controls operate exactly as they did before. Well almost- selecting the FWD/REV knob to centre with the motor running doesn't stop the motor. I have to hit the red stop button. I can live with that. I may move the speed control pot to a more convenient position if I get sick of leaning down to adjust the speed.

    I've also included a picture of my foot operated e-stop. A standard palm-operated stop switch mounted from behind the cabinet with a hinged wooden kick-plate.

    Thanks to everyone who offered advice.

    Chris
    Attached Images Attached Images
    Last edited by jack620; 27th June 2013 at 06:10 PM. Reason: extra info

  16. #105
    Join Date
    Oct 2012
    Location
    Australia
    Posts
    765

    Default

    Quote Originally Posted by jack620 View Post
    Stuart,
    thanks for looking into it for me. There is a parameter called Reverse Direction (rrS) which selects the logic input assigned to the reverse command (page 66). Default is Inactive. It wasn't easy to find, nor is it intuitively named.

    The VFD is now fully functional. All controls operate exactly as they did before. Well almost- selecting the FWD/REV knob to centre with the motor running doesn't stop the motor. I have to hit the red stop button. I can live with that. I may move the speed control pot to a more convenient position if I get sick of leaning down to adjust the speed.

    I've also included a picture of my foot operated e-stop. A standard palm-operated stop switch mounted from behind the cabinet with a hinged wooden kick-plate.

    Thanks to everyone who offered advice.

    Chris
    Chris
    So how did you end up wiring it up?

Page 7 of 9 FirstFirst ... 23456789 LastLast

Similar Threads

  1. Off machine switching
    By Anodyne in forum DUST EXTRACTION
    Replies: 4
    Last Post: 18th July 2011, 05:18 PM
  2. VSD/VFD forward reverse remote switching
    By eskimo in forum CNC Machines
    Replies: 4
    Last Post: 25th March 2010, 09:36 AM
  3. Need Source for 12V AC/DC Switching Adaptor
    By thumbsucker in forum COMPUTERS
    Replies: 6
    Last Post: 21st January 2009, 06:52 PM
  4. Switching Jaws
    By OGYT in forum WOODTURNING - GENERAL
    Replies: 44
    Last Post: 14th September 2007, 04:24 PM
  5. remote control switching for DC
    By Ironwood in forum DUST EXTRACTION
    Replies: 49
    Last Post: 10th November 2006, 11:13 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •