    Default um makes sence..

    your probably right. had not thought of it like that. what about the machine the motor is running at twice the speed. probably ok for a short time as well.
    do you loose much torque at over 50hz

    Quote Originally Posted by Ironwood View Post
    Hi Ray, I havent checked what F009 is set at now. If it is still at 3 percent ( factory setting) would you suggest to lower it ?

    I bought a new can of Aerogard this morning, broke the nozzle on the old can yesterday .



    From what I have read, it is common for people to set the max. Hz higher than 50Hz when fitting a VFD, to get a higher top speed.
    The 4 pole motors have a top speed of 1440 rpm at 50 Hz, I have been told they are using the same bearings as a 2 pole which is 2880 rpm at 50 Hz. So from what I have been led to believe, they can handle the higher speed.

    Someone please correct me if I am wrong here.

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #17
    Join Date
    Sep 2002
    Location
    Minbun, FNQ, Australia
    Age
    66
    Posts
    12,881

    Default

    Quote Originally Posted by Ironwood View Post
    Just checked Cliff, 242 volts at the VSD terminals while the motor is running at a slow speed....
    OK, cross that one off the list.
    Cliff.
    If you find a post of mine that is missing a pic that you'd like to see, let me know & I'll see if I can find a copy.

  4. #18
    Join Date
    Nov 2005
    Location
    adelaide
    Posts
    667

    Default

    i had a similar problem using an elcheapo chinese vfd if you set the motor amps at what the name plate( 1 .4 amps) said it would cut out with just a light cut .some where i read you should raise the motor current to a higher value which i did (5amps)and it fixed the problem .A very heavy cut only brings the current up to about 4.4 amps. it doesnt seem to have had any bad effects on the motor or vfd nothing gets overly warm
    john
    hmm i wonder if wired in delta config the amps should read 3 times the rated in star mode( 3x1.4=4.2)

  5. #19
    Join Date
    Apr 2006
    Location
    near Mackay
    Age
    59
    Posts
    4,635

    Default

    Quote Originally Posted by azzrock View Post
    your probably right. had not thought of it like that. what about the machine the motor is running at twice the speed. probably ok for a short time as well.
    do you loose much torque at over 50hz
    My lathe has a tapered roller bearing headstock, I am pretty sure it can run at high speeds for long periods of time.
    I guess you will have to make a call on your own machine, taking its design and condition into mind.

    I am not expecting to lose much torque at the Hz range I have set on the VFD.
    My VFD has vector control so I am hoping for good torque through a wide Hz range.
    From what I have read, I will lose torque at very low Hz, and also very high Hz.

  6. #20
    Join Date
    May 2010
    Location
    Sydney
    Posts
    78

    Default

    Quote Originally Posted by Cliff Rogers View Post
    Power = Voltage x Current

    Power/Voltage = Current
    actually there's a power factor correction in there as well, which for a motor running outside it's nameplate range could be quite low.

    If the motor is working at a power factor of less than about 0.7, a 1.1kW motor will overload a 1.5kW supply.

  7. #21
    Join Date
    Jul 2006
    Location
    Adelaide
    Posts
    2,680

    Default

    3.2amp no load seems too high

    How did you measure the voltage at motor terminals?...to terminal-earth or across each phase?

    did you measure all three phase current draws?

    Have you put a megger on the motor to ensure it doesnt have any leakage to earth?

    (I assume your using a 240 single phase to 240v - 3 phase vsd.)

  8. #22
    Join Date
    Apr 2006
    Location
    near Mackay
    Age
    59
    Posts
    4,635

    Default

    Quote Originally Posted by RayG View Post
    Just as an experiment, you could drop F009 back to 3% and switch back to V/F mode (F067=1) and see if the current goes back to what you were seeing originally.

    But, switching back to V/F mode, that's not really using the drive to it's potential.

    Regards
    Ray
    Checked the F009, it was set on 5. Set it back to 3, and ran the motor, it was an improvement, but still cut out on OL. I changed it back to 2, still cut out on OL when running at high speed.

    I changed back to V/F mode, that didnt seem to change the current at all, it still cut out on OL.

    I checked F068 ( vector voltage compensation) it has been set at 5 by the autotuning.


    F084 (power supply voltage) is factory set at 220 , I had never changed this before, but I set it to 240 today.
    This didnt seem to improve things.

  9. #23
    Join Date
    Apr 2006
    Location
    near Mackay
    Age
    59
    Posts
    4,635

    Default

    Quote Originally Posted by tanii51 View Post
    i had a similar problem using an elcheapo chinese vfd if you set the motor amps at what the name plate( 1 .4 amps) said it would cut out with just a light cut .some where i read you should raise the motor current to a higher value which i did (5amps)and it fixed the problem .A very heavy cut only brings the current up to about 4.4 amps. it doesnt seem to have had any bad effects on the motor or vfd nothing gets overly warm
    john
    hmm i wonder if wired in delta config the amps should read 3 times the rated in star mode( 3x1.4=4.2)
    I might have to try this also, before I did the autotuning, the problem wasnt evident.

  10. #24
    Join Date
    Apr 2006
    Location
    near Mackay
    Age
    59
    Posts
    4,635

    Default

    Quote Originally Posted by eskimo View Post
    3.2amp no load seems too high

    How did you measure the voltage at motor terminals?...to terminal-earth or across each phase?
    My Lecky mate was doing the testing while I operated the VSD, so I am not sure, but will check with him.

    Quote Originally Posted by eskimo View Post
    did you measure all three phase current draws?
    I remember him mentioning that all 3 phases were high, so I think he must have.

    Quote Originally Posted by eskimo View Post
    Have you put a megger on the motor to ensure it doesnt have any leakage to earth?

    (I assume your using a 240 single phase to 240v - 3 phase vsd.)
    A different Lecky mate tested the motor with his megger before I fitted it to the lathe. He said it was all good.

    The VSD is single phase to 220/240 3 phase. It was factory set at 220V supply, I changed it to 240V today.

  11. #25
    Join Date
    Jun 2008
    Location
    Victoria, Australia
    Age
    74
    Posts
    6,132

    Default

    Hi Ironwood,

    Not sure how easy it's going to be to try and figure out what the auto-tuning function has changed.

    Just checking...what values are entered for the number of poles F52, and of course.. the ratio of inverter rated current to motor rated current F78.

    Also while we are digging around, if you have time while dodging march flies..

    F1: acceleration time
    F2: deceleration time
    F10: rated frequency of motor (factory setting: 50Hz)
    F15 upper limit frequency

    F11 rated voltage % of motor

    F67: Operation Mode
    F68: vector voltage compensation
    F69: Slip compensation



    If all else fails... the next step...

    It's a drastic step, but it might be quicker to just reset the drive to factory defaults and re-commission it with the settings you originally entered.


    Regards
    Ray

  12. #26
    Join Date
    Oct 2010
    Location
    melbourne, laverton
    Posts
    1,469

    Default why was its top speed set lower then

    Quote Originally Posted by Ironwood View Post
    My lathe has a tapered roller bearing headstock, I am pretty sure it can run at high speeds for long periods of time.
    I guess you will have to make a call on your own machine, taking its design and condition into mind.

    .
    ya tapered bearing head stock. that's great so does one of mine.
    i just get concerned about the rest of the bearings in the machine. there is more than one shaft to worry about. are all the bearings in the head stock and feed box ect roller bearings? what sort of machine is it and why didn't they make it run twice as fast as they did.? i run my machine faster than the factory designed it but not for long and not more than 15 percent.. just interested because im setting one up as well.
    aaron
    .

  13. #27
    Join Date
    Apr 2006
    Location
    near Mackay
    Age
    59
    Posts
    4,635

    Default

    Quote Originally Posted by RayG View Post
    Hi Ironwood,

    Not sure how easy it's going to be to try and figure out what the auto-tuning function has changed.

    Just checking...what values are entered for the number of poles F52, and of course.. the ratio of inverter rated current to motor rated current F78.

    Also while we are digging around, if you have time while dodging march flies..

    F1: acceleration time
    F2: deceleration time
    F10: rated frequency of motor (factory setting: 50Hz)
    F15 upper limit frequency

    F11 rated voltage % of motor

    F67: Operation Mode
    F68: vector voltage compensation
    F69: Slip compensation



    If all else fails... the next step...

    It's a drastic step, but it might be quicker to just reset the drive to factory defaults and re-commission it with the settings you originally entered.


    Regards
    Ray
    Hi Ray, I will try to answer all your questions I can, without going back down to the shed.
    F52 - I havent changed this, so assume its still on factory setting of 4 (its a 4 pole motor by the way)
    F78 - I have set this to 55, my calculations are 4.7 is 55 percent of 7 (am I on the right track here?)

    F1 - I have set to 3
    F2 - I have set to 2
    F10 - left at 50
    F11 - 100
    F67 - autotuning has set this to 3 ( I have tried resetting back to 1, but the high current draw continues )
    F68 - autotuning has set this to 5
    F69 - I havent checked this one, will look tomorrow.

    Regarding the resetting the factory defaults, I have decided I will go down that path when I get home from work tomorrow. This problem wasnt evident before I did the autotuning.
    I dont know what the current was before I did the autotuning, as I only started to check once the lathe was cutting out on OL.

    I have reset F51 back to 10 seconds, I think autotuning set it to 30. Before it cuts out after 10 seconds above 4.7 amps, the current does go up above 6 amps if the pot. is turned up quickly.

  14. #28
    Join Date
    Jun 2008
    Location
    Victoria, Australia
    Age
    74
    Posts
    6,132

    Default

    Quote Originally Posted by Ironwood View Post
    F78 - I have set this to 55, my calculations are 4.7 is 55 percent of 7 (am I on the right track here?)
    I would have gone for 70% rounded up from (4.7/7)*100 = 67

    Regards
    Ray

  15. #29
    Join Date
    Apr 2006
    Location
    near Mackay
    Age
    59
    Posts
    4,635

    Default

    Quote Originally Posted by RayG View Post
    I would have gone for 70% rounded up from (4.7/7)*100 = 67

    Regards
    Ray
    No worries, so that could be causing, or contributing to the problem.

    Should have gone looking for that calculator instead of figuring it out in my head

  16. #30
    Join Date
    Jun 2008
    Location
    Victoria, Australia
    Age
    74
    Posts
    6,132

    Default

    Hi Ironwood,

    Well it could possibly be the problem, using 55% you would be effectively setting the rated motor current to 3.85 amps. instead of 4.7 amps

    So you will get instantaneous trip at 5.8 amps instead of 7.4 amps, that might do it.

    That's assuming I'm reading page 8 of the manual correctly.


    The whole purpose of this protection, is just to protect the motor, from overcurrent, i would leave F51 at 30 seconds.

    The other thing I meant to ask, and that is, when it trips what is the exact error number?

    Regards
    Ray

Page 2 of 4 FirstFirst 1234 LastLast

Similar Threads

  1. Kit problems
    By Treecycle in forum WOODTURNING - PEN TURNING
    Replies: 5
    Last Post: 4th November 2010, 08:05 AM
  2. BBQ Problems
    By tergar37 in forum METALWORK FORUM
    Replies: 1
    Last Post: 17th September 2010, 10:09 PM
  3. Big Problems
    By mick61 in forum COMPUTERS
    Replies: 1
    Last Post: 25th February 2010, 11:14 PM
  4. More problems
    By artme in forum HEALTH ISSUES
    Replies: 3
    Last Post: 3rd March 2009, 10:00 PM
  5. CA problems
    By Big Shed in forum WOODTURNING - PEN TURNING
    Replies: 15
    Last Post: 13th July 2008, 07:10 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •