    Default Earthing dust extraction

    Hi all

    I am in the process of setting up my workshop and have heard and seen a bit about the need to earth plastic dust extraction pipes to prevent static sparkes and subsequent fires?

    Do you all do this and if not why?

    I have seen a few cable kits and considering I would prefer that my workshop not burn down am thinking this is the thing to do.

    What exactly is it that you earth? Do you attach the cable from the plastic pipe at one end and drill a hole into the ground for the other? I am on a concrete slab, will this still earth properly??

    And I thought woodworking was about wood not being an electrician!!

    Thanks

    Cam

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Dec 2008
    Location
    Tasmania
    Posts
    430

    Default Earthing dust extractor system

    Hi Chief 012,

    I've seen the arguments for and against earthing dust extractors with plastic pipe reticulation rattle round for many years. I've never seen anything definitive come forward on this and it certainly doesn't form part of the requirements of my insurer. I've been going along sucking dust most days for 27 years without any problem and without an earth in place.There's certainly lots of static there on the outside of the pipes:sufficient to make the hairs on my wrists stand up on end if placed about 100mm or less distance from the pipe.

    That's all I know about it. Let us all know if you find the answer.

    Old Pete

  4. #3
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,793

    Default

    In terms of hobby and non-industrial DCs it's a myth that static electricity produced by PVC ducting will cause a fire/explosion. It is also physically impossible to ground PVC since it is an insulator so using the cable kits on PVC is waste of money.

    For a technical discussion by MIT Physicist Rod Cole see here.

    Fires do occur in DCs but the happen for other reasons like sucking in a lump of hot metal, overheating the DC motor etc

  5. #4
    Join Date
    Sep 2006
    Location
    Newcastle
    Posts
    192

    Default

    Thanks old pete & BobL, I think you have well and truly answered my question there!

    From Rod Cole's article - I should be just as concerned about spontaneous compustion!

    Many thanks

    Cam

  6. #5
    Join Date
    Apr 2002
    Location
    Brisbane
    Posts
    5,773

    Default

    Inaddition Mythbusters did a segment on static in plastic pipes and possible ignition........BUSTED.

    As I have posted before......no one has ever produced a single documented incident where there has been a dust explosion in small scale workshop dust extracion systems due to static electricity.

    cheers
    Any thing with sharp teeth eats meat.
    Most powertools have sharp teeth.
    People are made of meat.
    Abrasives can be just as dangerous as a blade.....and 10 times more painfull.

  7. #6
    Join Date
    Jun 2005
    Location
    Helensburgh
    Posts
    7,696

    Default

    This question comes up a lot in discussion and planning systems. Systems vary, some suffer, mine certainly doesn't and no one seems to have any answers. An insulator can't be grounded, my system hangs from a metal roof structure and I have always wondered if that has anything to do with it never generating static electricity, I don't see how it can as that metal structure sits on a timber frame.
    CHRIS

  8. #7
    Join Date
    Sep 2006
    Location
    Newcastle
    Posts
    192

    Default

    Got to love Mythbusters!

    I did not earth mine and am happy to say I am still here to tell the tale

  9. #8
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,793

    Default

    The main reason that a small cavity like PVC ducting does not generate a spark inside itself is because as soon as any charge builds up inside it the charge moves to the outside of that cavity so not enough charge builds up on the inside to generate a spark. Even if a spark is generate the air-dust ratio required for explosion are relatively narrow.

    On a dry day it is possible to feel the charge on the outside of dusty ducting and it may give you a bite which is why some people like to ground their ducting.

    With plastic ducting there is a miniscule chance that two chunks of say steel and stone will impact together or more likely that stone will strike the steel impeller and make a spark. Grounding of the ducting will do nothing for this potential problem and is one of several reasons not to use your DC as a vacuum cleaner.

    In situations where large steel ducting is used the cavities are much larger, the air speeds often higher resulting in greater amounts of charge and there are often lots of sharp points near ports and junctions where a discharge may lead to sparks.

  10. #9
    Join Date
    Nov 2006
    Location
    Rockhampton
    Age
    62
    Posts
    2,236

    Default

    I haven't earthed mine, I have a combination of metal and plastic pipe, I do get a bit of static build up in the plastic pipes off the thicky but nothing that concerns me, I get more of a zap getting out of the car

    The general concensus is you don't need to bother, if you want to do it for some piece of mind or don't like getting zapped, OK do it but I had conditions that if my DE was going to catch fire I had it here https://www.woodworkforums.com/f200/w...-there-135446/ and no fire/explosion.


    Pete

  11. #10
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,793

    Default

    Quote Originally Posted by pjt View Post
    I haven't earthed mine, I have a combination of metal and plastic pipe, I do get a bit of static build up in the plastic pipes off the thicky but nothing that concerns me, I get more of a zap getting out of the car
    . . .
    Sorry to be pedantic but else one uses a particle accelerator, it is not possible to get build up of charge "in" plastic or inside a plastic pipe, it can only build up "on the outside" of the plastic pipe. I'm only being pedantic in case some newbie reading you post thinks it can build up inside the ducting

  12. #11
    Join Date
    Nov 2006
    Location
    Rockhampton
    Age
    62
    Posts
    2,236

    Default

    Quote Originally Posted by BobL View Post
    Sorry to be pedantic but else one uses a particle accelerator, it is not possible to get build up of charge "in" plastic or inside a plastic pipe, it can only build up "on the outside" of the plastic pipe. I'm only being pedantic in case some newbie reading you post thinks it can build up inside the ducting

    Nope, no particle accelerator here, I guess it's just one of those things that most of us say that isn't technically correct but is just said, like the difference between absorbed and adsorbed, most would know absorb but may not know adsorb and therefore say something like " the liquid was absorbed" into the cloth but in fact it may have only been adsorbed


    Pete

  13. #12
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,793

    Default

    Quote Originally Posted by pjt View Post
    Nope, no particle accelerator here, I guess it's just one of those things that most of us say that isn't technically correct but is just said, like the difference between absorbed and adsorbed, most would know absorb but may not know adsorb and therefore say something like " the liquid was absorbed" into the cloth but in fact it may have only been adsorbed


    Pete
    Yep - I get that one confused from time to time.

  14. #13
    Join Date
    Oct 2003
    Location
    Sydney,Australia
    Posts
    3,157

    Default

    The one possible use for grounding PVC pipe systems is avoiding the 'Youch!' effect when getting zapped by the static.

    But no fire.

  15. #14
    Join Date
    Apr 2002
    Location
    Brisbane
    Posts
    5,773

    Default

    Um yeh it wont even do that.

    Ya cant earth PVC because it is not conductive and parts will still build up charge.

    There are arguments that attempting to earth a PVC dust extraction system actuall increses the hazards.

    cheers
    Any thing with sharp teeth eats meat.
    Most powertools have sharp teeth.
    People are made of meat.
    Abrasives can be just as dangerous as a blade.....and 10 times more painfull.

Similar Threads

  1. Dust extraction
    By Tiger in forum DUST EXTRACTION
    Replies: 6
    Last Post: 26th April 2005, 07:57 PM
  2. Dust Extraction
    By SteveAndBelle in forum TRITON / GMC
    Replies: 16
    Last Post: 23rd March 2005, 06:54 PM
  3. dust extraction
    By Redback in forum TRITON / GMC
    Replies: 5
    Last Post: 26th February 2005, 04:26 PM
  4. Dust Extraction
    By barnsey in forum DUST EXTRACTION
    Replies: 1
    Last Post: 25th August 2003, 09:41 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •