Likes Likes:  0
Needs Pictures Needs Pictures:  0
Picture(s) thanks Picture(s) thanks:  0
Results 1 to 5 of 5
  1. #1
    Join Date
    Dec 2004
    Location
    Northen Rivers NSW
    Age
    57
    Posts
    2,837

    Default Is this a structural internal wall

    Howdy everyone

    Is it possible to tell if the wall marked on these plans is structural or not?

    Kindest regards

    Homer







    The green wall is the one I am talking about. You can see the huge beam in the foreground painted white. I imagine from the plans that the rafters run from the external wall across to that beam.
    (Are they still called rafters in that type of ceiling - vaulted?)




    And I found another plan;





    Sent from my iPad using Tapatalk


  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Age
    2010
    Posts
    Many





     
  3. #2
    Join Date
    May 2011
    Location
    Albury
    Posts
    3,034

    Default

    I suspect it's impossible to tell from the information available on those plans. It looks like the rafters are 150 x 45 LVL's @ 600 centres, but we don't know what the span or roof load is. It appears from what you've provided that there are a couple of rafter spans in that roof section that are only supported at the ends, but to offer an opinion without further info. would be a bold step. The roof may have been designed by a structural engineer as a unit. If the wall is load bearing can the 112 x 112 laminated post in the living room and the 230 x 65 laminated beam it supports support any additional loads? Who knows?

    Call in the experts to have a look.

  4. #3
    Mobyturns's Avatar
    Mobyturns is offline In An Instant Your Life Can Change Forever
    Join Date
    Jul 2012
    Location
    "Brownsville" Nth QLD
    Age
    66
    Posts
    4,426

    Default

    Quote Originally Posted by aldav View Post
    Call in the experts to have a look.
    Good advice!

    Without the drawings for Section's A, B & C its a guessing game.

    Best approach is to contact your local authority / building certifier to obtain the "approved" plans and structural engineers report for the previous renovations, and the certifying authorities inspection report / approval sign off. That will have all the info you require, then its only a matter of verifying that nothing has changed.

    Given the "150 x 45 LVL @ 600 max crs" note and that the rafters span the whole of that Family / Bedroom / Deck area its probable that the wall may not be load bearing - however it may be a bracing wall for wind loading.
    Mobyturns

    In An Instant Your Life CanChange Forever

  5. #4
    Join Date
    Apr 2018
    Location
    Nsw
    Age
    64
    Posts
    1,361

    Default

    Do not rely on your plans or the ones the council has on file, they don’t necessarily reflect what actually happened on site. Changes get made all the time that are not documented on file
    Use the plans by all means as a guide but you really need to get in the roof / remove a sheet etc if necessary to confirm what is there and how it is supported.

    If the premise of the question is to see if you can remove or create an opening in the wall I don’t see that as being an issue. An appropriate lintel beam can be installed if necessary to support the load.

  6. #5
    Join Date
    Dec 2004
    Location
    Northen Rivers NSW
    Age
    57
    Posts
    2,837

    Default

    Thanks all

    Advice really appreciated.

    I have to get some external work approved so will add removal of this wall to the plans. A lintel will be fine, as there is another one on the opposite side of the room near the kitchen so it will not look out of place.

    Cheers!


Similar Threads

  1. non structural wall
    By Tonyz in forum WOODWORK - GENERAL
    Replies: 11
    Last Post: 31st December 2018, 11:26 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •