    Default making neat connections?

    Hi all, been practicing some wiring connections before I do the real thing on installing a bunch of fluoro downlights, oysters and halogens in an extension I've been owner building for a while now. All the wiring is brand new and at this stage the final connection to live power has NOT been made. So far I've done all the switches without any dramas ensuring that i twist up the 1.5mm stranded red/white switch wires then where they are single wires and folding them over to go into the switch terminals.
    Now its time to do the light fittings i'm using junction boxes on all the lights as most of them dont have the capacity to take more than 1 cable and because several of them have power in/power out/and shoot off to an extra fitting the need to twist up 3 wires plus a tail for the fitting and total 4 x1.5mm wires i felt it best to use J boxes rather than taping up connections. i hate the thought of twisting 4 wires together but I'm assuming its neccesary and have seen it done in many other locations in the existing part of the house (mainly in bayonetts).
    Anyway I have enclosed 2 photos to see if anyone feels my technique is poor or not. So what i have in the photo is 4x neutrals, 4x earths, 4x actives(1 is the switch wire) then a red wire from the tail cable joined to the white switch wire. I know the sequence is fine i'm just not sure if the workmanship is up to standard so i'm helping the gurus in here can give their opinion, In a nutshell, what is the trick to twisting 4 x 1.5mm stranded wires together (fan the whole lot together or twist individually then all together) and does it REALLY matter too much if they look pretty or not since their being locked up with double screw connectors? Is this where potential fire risk can exist or not..... ....be kind guys.

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Aug 2006
    Location
    Australia
    Posts
    72

    Default

    Whilst its obviously illegal to do your own electrical work unless its inspected by a licenced electrician and all that jazz, we can talk hyperthetically about the best way to make connections.

    From those pictures, it looks like your doing a good job. To twist 4 conductors together, keep them faned, dont twist individually first.
    I accept no liability or responsibility for advice offered by myself regarding Electrical or Airconditioning related questions. I strongly advise contacting a Licensed Tradeperson for all work of this nature.

  4. #3
    Join Date
    Oct 2003
    Location
    Kentucky NSW near Tamworth, Australia
    Age
    85
    Posts
    3,737

    Default

    You and I are going to get flamed here because you shouldn't be doing it yourself because you are obviously not a sparky and I shouldn't be giving you advice but my trouble is I can't help myself.

    But the ends of the insulation should be lined up and the shrouds of the connectors should fully cover the copper wire which they don't so they don't comply..

    My advice get a sparky.

    Another thing I just noticed is that you have used earth connectors on all the connections. Probably doesn't matter.

    It appears cross who says he is an apprentice electrician doesn't agree but I wouldn't accept it on my place.
    Last edited by Barry_White; 2nd March 2007 at 05:49 PM. Reason: Another comment

  5. #4
    Join Date
    Aug 2006
    Location
    Australia
    Posts
    72

    Default

    But the ends of the insulation should be lined up and the shrouds of the connectors should fully cover the copper wire which they don't so they don't comply..
    Agh, the magic of zooming in. Had a closer look at the pictures and take back my previous comments.

    Another thing I just noticed is that you have used earth connectors on all the connections. Probably doesn't matter.
    It doesnt matter, its required for the earth, but not the others, although its fine to use them for all (providing your not using the double screw to make up for lack of twisting ability ).
    I accept no liability or responsibility for advice offered by myself regarding Electrical or Airconditioning related questions. I strongly advise contacting a Licensed Tradeperson for all work of this nature.

  6. #5
    Join Date
    Aug 2006
    Location
    Sydney
    Age
    64
    Posts
    2,378

    Default

    What Barry and Cross have said.

    Actually I just wanted to show off my new signiture.

    I didn't think it was right not to have a disclaimer at the end of this post.

  7. #6
    Join Date
    Aug 2006
    Location
    Australia
    Posts
    72

    Default

    Quote Originally Posted by Bleedin Thumb View Post
    What Barry and Cross have said.

    Actually I just wanted to show off my new signiture.

    I didn't think it was right not to have a disclaimer at the end of this post.
    Nice one.
    I accept no liability or responsibility for advice offered by myself regarding Electrical or Airconditioning related questions. I strongly advise contacting a Licensed Tradeperson for all work of this nature.

  8. #7
    Join Date
    Jan 2005
    Location
    Brisbane
    Age
    52
    Posts
    468

    Default

    I would not install the lights as you have suggested. I would not be happy with that joint sitting in my ceiling. Not because it is especially safe, rather it represents a higher risk, as it doesn't reflect best practice.

    I think that you are going about this the 'hard' way.

    The majority of sparky's will twin and earth rather than dedicated switching wire, especially in brown field sites.

    Generally, hypothetically If i was asked to do this install my preference would be to diasy chain them for a maximum of two connections per light. One cable coming from the switch. Less cable less mess. Also no J box, significantly less chance of a hot joint...



    I'd also only use double screw connectors on the earths. I'd also tape the connections, green and gold for the earth and black for the others...

    If you are going to do this yourself, stay safe, remember a little bit of knowledge can be dangerous....

    PS. I will be doing some electrical work in Wollongong next week.......

    I accept no liability or responsibility for advice offered by myself regarding Electrical related questions. I strongly advise contacting a Licensed Tradeperson for all work of this nature.
    Last edited by spartan; 2nd March 2007 at 08:10 PM. Reason: political correctness

  9. #8
    Join Date
    Aug 2005
    Location
    Victoria
    Posts
    664

    Default

    Are those double screw connectors sealed on one end? A lot of them have a hole right through.

    Tools

  10. #9
    Join Date
    Oct 2003
    Location
    Kentucky NSW near Tamworth, Australia
    Age
    85
    Posts
    3,737

    Default

    Quote Originally Posted by Tools View Post
    Are those double screw connectors sealed on one end? A lot of them have a hole right through.

    Tools
    The double screw earth connectors do have a hole at both ends. Single screw connectors are blind so that the Active and neutral wires cannot be exposed.

  11. #10
    Join Date
    Feb 2007
    Location
    wollongong
    Posts
    10

    Default

    Ok gents took most of your advice onboard,except the one to get in a licensed eleco (rang a few and at $60 an hour have opted to trust my workmanship for the time being). I got rid of the double screw connectors except for the one on the earth and replaced them with single blind ones( as supplied in the J box), Red taped the active connector for safeguard and housed the whole lot neatly in a J box. I'm pretty happy with it but have supplied a pic so youz can either believe me lol or attack me lol. Thanks a lot guys, much appreciated.

  12. #11
    Join Date
    Feb 2006
    Location
    Melbourne
    Age
    65
    Posts
    979

    Default

    I dont have a clue about anything. If you take my advise seriously you're a fool. If you act on my advise and get killed you're a bigger fool. Don't bother suing me as I have no assets.

    Hi Bleeding Thumb,

    Without sounding too pedantic, you should change advise to advice or you maybe sued.<!-- / sig -->

  13. #12
    Join Date
    Oct 2003
    Location
    Kentucky NSW near Tamworth, Australia
    Age
    85
    Posts
    3,737

    Default

    Quote Originally Posted by Metal Head View Post
    I dont have a clue about anything. If you take my advise seriously you're a fool. If you act on my advise and get killed you're a bigger fool. Don't bother suing me as I have no assets.

    Hi Bleeding Thumb,

    Without sounding too pedantic, you should change advise to advice or you maybe sued.<!-- / sig -->
    That's very interesting Bleeding picked me up on my spelling a while ago on exactly the same spelling mistake.

    Like they say "What goes around comes around." LOL

  14. #13
    Join Date
    Aug 2006
    Location
    Sydney
    Age
    64
    Posts
    2,378

    Default

    Quote Originally Posted by Barry_White View Post
    That's very interesting Bleeding picked me up on my spelling a while ago on exactly the same spelling mistake.

    Like they say "What goes around comes around." LOL

    Don't think it was me Barry, it would be like the pot calling the kettle black for me to criticize anybodies spelling.

    I have to thank you BTW for the tip regarding the spell checker on the Google bar - very handy.

    I'll go back and edit the spelling Metal Head, even though I think the signiture is due for a change.

  15. #14
    Join Date
    Oct 2003
    Location
    Kentucky NSW near Tamworth, Australia
    Age
    85
    Posts
    3,737

    Default

    Quote Originally Posted by Bleedin Thumb View Post
    Don't think it was me Barry, it would be like the pot calling the kettle black for me to criticize anybodies spelling.

    I have to thank you BTW for the tip regarding the spell checker on the Google bar - very handy.

    I'll go back and edit the spelling Metal Head, even though I think the signiture is due for a change.
    I apologise Bleeding it wasn't you. I tracked down the culprit and at least he did it with a PM rather than publicly so I wont reveal who it was.

  16. #15
    Join Date
    Jan 2005
    Location
    Brisbane
    Age
    52
    Posts
    468

    Default

    Jag, see my earlier comments.

    Whilst this will work it is very obvious that it wasn't done by a knowledgable electrician.

    Whatever you decide to do stay safe.

Page 1 of 2 12 LastLast

Similar Threads

  1. Pen making advice...?
    By Steve Walkom in forum WOODTURNING - GENERAL
    Replies: 10
    Last Post: 20th May 2006, 07:12 PM
  2. Making shoulder planes
    By Arron in forum WOODWORK - GENERAL
    Replies: 21
    Last Post: 10th December 2005, 05:53 AM
  3. Dust Collection - Machinery Connections
    By bitingmidge in forum DUST EXTRACTION
    Replies: 136
    Last Post: 12th September 2005, 09:54 PM
  4. Making a Better Coping/Dovetail Saw
    By Bob Smalser in forum HAND TOOLS - UNPOWERED
    Replies: 7
    Last Post: 7th October 2004, 12:38 PM
  5. Book recomendations - Table making
    By DaveInOz in forum WOODWORK - GENERAL
    Replies: 8
    Last Post: 1st October 2004, 02:45 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •